Features and specifications

Use this information for an overview of the chassis features and specifications.

The following information is a summary of the features and specifications of the chassis. Depending on the model, some features might not be available, or some specifications might not apply.

Node bays (on front):

The chassis has twelve node bays.

Module bays (on rear):
  • Six hot-swap power-supply bays
  • Ten hot-swap fan bays
Cooling:

Supports ten hot-swap fan modules.

Upgradeable microcode:

Microcode is upgradeable when fixes or features are added.

  • Compute node firmwares
  • FPC firmware
Power supplies:
  • Supports six hot-swap AC and DC power supplies
    • 900-watt AC
    • 1300-watt AC platinum
    • -48V 900-watt DC
Note:
  • Power supplies in the chassis must be with the same input voltage range, power rating, and certification category.
  • 1300-watt power supplies support high-line Vin (AC 200V – 240V) only.
Electrical input:
  • Sine-wave input (50/60 Hz) required
  • Input voltage low range:
    • Minimum: 100 V AC
    • Maximum: 127 V AC
  • Input voltage high range:
    • Minimum: 200 V AC
    • Maximum: 240 V AC
  • Input kilovolt-amperes (kVA), approximately:
    • Minimum: 0.14 kVA
    • Maximum: 1.19 kVA
Security features:
  • Login password for remote connection
  • Secure Sockets Layer (SSL) security for remote management access
  • Trusted and signed firmware
Predictive Failure Analysis (PFA) alerts:
  • Fan modules
  • Compute-node dependent features
  • Power supply modules
Size (6U):
  • Height: 263.3 mm (10.37 in.)
  • Depth: 914.5 mm (36 in.)
  • Width: 447 mm (17.6 in.)
  • Weight:
    • Fully configured (stand-alone): approximately 112 kg (247 lb)
    • Empty chassis (with midplant, FPC, and cables): approximately 28 kg (62 lb)
Approximate heat output::
Approximate heat output:
  • Minimum configuration: 1365 Btu per hour (400 watts)
  • Maximum configuration: 24,565 Btu per hour (7,200 watts)
Declared sound power level:
  • 7.5 bels
Chassis airflow:

Full chassis configuration with all nodes, fan power control, power supplies, and fan modules installed.

  • Minimum - 158 CFM (at the idle state)
  • Nominal - 213 CFM (at the acoustic fan speed)
  • Maximum - 614 CFM (at the fan full speed)
Environment:
The NeXtScale n1200 Enclosure complies with ASHRAE class A3 specifications.
  • Power on 1:
    • Temperature: 5°C - 40°C (41°F - 104°F) 3
    • Humidity, non-condensing: -12°C dew point (10.4°F) and 8% - 85% relative humidity 5,6
    • Maximum dew point: 24°C (75°F)
    • Maximum altitude: 3048 m (10,000 ft)
    • Maximum rate of temperature change: 5°C/hr (41°F/hr ) 4
  • Power off 2:
    • Temperature: 5°C to 45°C (41°F - 113°F)
    • Relative humidity: 8% - 85%
    • Maximum dew point: 27°C (80.6°F)
  • Storage (non-operating):
    • Temperature: 1°C to 60°C (33.8°F - 140°F)
    • Altitude: 3050 m (10,006 ft)
    • Relative humidity: 5% - 80%
    • Maximum dew point: 29°C (84.2°F)
  • Shipment (non-operating) 7:
    • Temperature: -40°C to 60°C (-40°F - 140°F)
    • Altitude: 10,700 m (35,105 ft)
    • Relative humidity: 5% - 100%
    • Maximum dew point: 29°C (84.2°F) 8
Note:
  1. Chassis is powered on.
  2. Chassis is removed from original shipping container and is installed but not in use, for example, during repair, maintenance, or upgrade.
  3. A3 - Derate maximum allowable temperature 1°C/175 m above 950 m.
  4. 5°C/hr for data centers employing tape drives and 20°C/hr for data centers employing disk drives.
  5. The minimum humidity level for class A3 is the higher (more moisture) of the -12 °C dew point and the 8% relative humidity. These intersect at approximately 25°C. Below this intersection (~25C) the dew point (-12 °C) represents the minimum moisture level, while above it relative humidity (8%) is the minimum.
  6. Moisture levels lower than 0.5°C DP, but not lower -10 °C DP or 8% relative humidity, can be accepted if appropriate control measures are implemented to limit the generation of static electricity on personnel and equipment in the data center. All personnel and mobile furnishings and equipment must be connected to ground via an appropriate static control system. The following items are considered the minimum requirements:
    1. Conductive materials (conductive flooring, conductive footwear on all personnel that go into the datacenter, all mobile furnishings and equipment will be made of conductive or static dissipative materials).
    2. During maintenance on any hardware, a properly functioning wrist strap must be used by any personnel who contacts IT equipment.
  7. The equipment acclimation period is 1 hour per 20 °C of temperature change from the shipping environment to the operating environment.
  8. Condensation is acceptable, but not rain.
  9. Power consumption and heat output vary depending on the number and type of optional features installed and the power-management optional features in use.
  10. The noise emission level stated is the declared (upper limit) sound power level, in bels, for a random sample of machines. All measurements are made in accordance with ISO 7779 and reported in conformance with ISO 9296. Actual sound-pressure levels in a given location might exceed the average values stated because of room reflections and other nearby noise sources. The noise emission level stated in the declared (upper limit) sound-power level, in bels, for a random sample of system.