To install a hot-swap DC power supply, complete the following
steps.
- Only trained service personnel other than Lenovo service technicians
are authorized to install and remove the -48 volt DC power supply,
and make the connections to and disconnections from the -48 volt DC
power source. Lenovo service technicians are not certified or authorized
to install or remove the -48 volt power cable. The customer is responsible
for ensuring that only trained service personnel install or remove
the -48 volt power cable.
- Before you install a DC power supply in the server, you must remove
all AC power supplies. Do not use both AC and DC power supplies in
the same server. Install six DC power supplies or six AC power supplies,
but not a combination.
- If you need to order more ferrite clamp cores, the part number
is 94Y8175.
Regulations
- It is the customer's responsibility to supply the necessary power
cable.
To reduce the risk of electric shock or energy hazards:
- Use a circuit breaker that is rated at 70 amps.
- Use 4 mm2 (10 AWG) at 90° C copper wire.
- Torque the wiring-terminal screws to 0.50 ~ 0.60 newton-meters
(4.43 ~ 5.31 inch-pounds).
For more information, see Statement 34.
- If the power source requires ring terminals, you must use a crimping
tool to install the ring terminals to the power cord wires. The ring
terminals must be UL approved and must accommodate the wire that is
described in the above-mentioned note.
- To avoid radiated emission, you must attach a clamp core for each
of the 900 W DC power supply used.
Figure 1. Ferrite clamp core
Statement 29CAUTION: This equipment is designed to permit the connection of
the earthed conductor of the DC supply circuit to the earthing conductor
at the equipment.
This equipment is designed to permit the
connection of the earthed conductor of the DC supply circuit to the
earthing conductor at the equipment. If this connection is made, all
of the following conditions must be met:
- This equipment shall be connected directly to the DC supply system
earthing electrode conductor or to a bonding jumper from an earthing
terminal bar or bus to which the DC supply system earthing electrode
conductor is connected.
- This equipment shall be located in the same immediate area (such
as, adjacent cabinets) as any other equipment that has a connection
between the earthed conductor of the same DC supply circuit and the
earthing conductor, and also the point of earthing of the DC system.
The DC system shall not be earthed elsewhere.
- The DC supply source shall be located within the same premises
as this equipment.
- Switching or disconnecting devices shall not be in the earthed
circuit conductor between the DC source and the point of connection
of the earthing electrode conductor.
Statement 31DANGER
Electrical current from power,
telephone, and communication cables is hazardous.
To avoid a
shock hazard:
- Do not connect or disconnect any cables or perform installation,
maintenance, or reconfiguration of this product during an electrical
storm.
- Connect all power cords to a properly wired and grounded power
source.
- Connect to properly wired power sources any equipment that will
be attached to this product.
- When possible, use one hand only to connect or disconnect signal
cables.
- Never turn on any equipment when there is evidence of fire, water,
or structural damage.
- Disconnect the attached ac power cords, dc power sources, network
connections, telecommunications systems, and serial cables before
you open the device covers, unless you are instructed otherwise in
the installation and configuration procedures.
- Connect and disconnect cables as described in the following table
when you install, move, or open covers on this product or attached
devices.
To Connect: |
To Disconnect: |
- Turn OFF all power sources and equipment that is to be attached
to this product.
- Attach signal cables to the product.
- Attach power cords to the product.
- For ac systems, use appliance inlets.
- For dc systems, ensure correct polarity of -48 V dc connections:
RTN is + and -48 V dc is -. Earth ground should use a two-hole lug
for safety.
- Attach signal cables to other devices.
- Connect power cords to their sources.
- Turn ON all the power sources.
|
- Turn OFF all power sources and equipment that is to be attached
to this product.
- For ac systems, remove all power cords from the chassis power
receptacles or interrupt power at the ac power distribution unit.
- For dc systems, disconnect dc power sources at the breaker panel
or by turning off the power source. Then, remove the dc cables.
- Remove the signal cables from the connectors.
- Remove all cables from the devices.
|
Statement 33CAUTION:
This product does not provide
a power-control button. Turning off blades or removing power modules
and I/O modules does not turn off electrical current to the product.
The product also might have more than one power cord. To remove all
electrical current from the product, make sure that all power cords
are disconnected from the power source.
Statement 34CAUTION:
To reduce the risk
of electric shock or energy hazards:
- This equipment must be installed by trained service personnel
in a restricted-access location, as defined by the NEC and IEC 60950-1,
First Edition, The Standard for Safety of Information Technology Equipment.
- Connect the equipment to a properly grounded safety extra low
voltage (SELV) source. A SELV source is a secondary circuit that
is designed so that normal and single fault conditions do not cause
the voltages to exceed a safe level (60 V direct current).
- Incorporate a readily available approved and rated disconnect
device in the field wiring.
- See the specifications in the product documentation for the required
circuit-breaker rating for branch circuit overcurrent protection.
- Use copper wire conductors only. See the specifications in the
product documentation for the required wire size.
- See the specifications in the product documentation for the required
torque values for the wiring-terminal screws.