Use this information for an overview of the server features
and specifications.
The following information is a summary of the features
and specifications of the server. Depending on the model, some features
might not be available, or some specifications might not apply.
- Microprocessor (depending on the model):
- Supports two Intel® Xeon™ E5-2600 v3 or
two Intel Xeon™ E5-2600 v4 series
multi-core microprocessors per system board
- Level-3 cache
- Two QuickPath Interconnect (QPI) links speed up to 9.6 GT per
second
Note:
- Use the Setup utility to determine the type and speed of the microprocessors
in the server
- For a list of supported microprocessors, see the IBM ServerProven website.
- Memory:
- 16 dual inline memory module (DIMM) connectors available per
system board
- Type: Low-profile (LP) double-data rate (DDR4) DRAM
- Supports 8 GB / 16 GB RDIMMs and 32 GB DIMMs with up to 512 GB
of total memory on the system board
- PCI expansion slots:
- One PCI Express x16 slots (PCIe3.0, full-height, half-length,
limited to specific adapters) per system board
- One PCI Express x16 (ML2) slots (support 50 mm in height only) per
system board
- Power supplies:
- Supports six hot-swap ac power supplies
- 1300-watt ac
- 1500-watt ac
Note:
- Power supplies in the chassis must be with the same power rating
or wattage.
- Integrated functions:
- Integrated management module 2.1 (IMM2.1), which consolidates
multiple management functions in a single chip
- Concurrent COM/VGA/2x USB (KVM)
- System error LEDs
- Supports up to two optional ML2 network adapter
- Wake on LAN (WOL)
- Video controller (integrated into IMM2.1):
- Matrox G200eR2
- SVGA compatible video controller
- Avocent Digital Video Compression
- Video memory is not expandable
Note: Maximum video resolution is 1600 x 1200 at 75 Hz.
- Size:
- Height: 41 mm (1.6 in)
- Depth: 742 mm (29.2 in)
- Width: 438 mm (17.25 in)
- Weight estimation: 13.3 kg (29.3 lb)
- Acoustical noise emissions:
Sound
power: 7.0 bels
- Environment:
The water-cooled technology tray complies with ASHRAE class A3 specifications.
Storage (non-operating):
- Temperature: 1°C to 60°C (33.8°F to 140.0°F)
- Maximum altitude: 3,050 m (10,000 ft)
- Relative humidity: 5% to 80%
- Maximum dew point: 29°C (84.2°F)
Shipment (non-operating):
- Temperature: -40°C to 60°C (-40°F to 140.0°F)
- Maximum altitude: 10,700 m (35,105 ft)
- Relative humidity: 5% to 100%
- Maximum dew point: 29°C (84.2°F)
Server off:
- Temperature: 5°C to 45°C (41°F to 113°F)
- Relative humidity: 8% to 85%
- Maximum dew point: 27°C (80.6°F)
Server on
- Temperature: 5°C to 40°C (41°F to 104°F) up to 950 m
- Humidity, non-condensing: -12°C dew point (10.4°F) and 8% to 85%
relative humidity
- Maximum dew point: 24°C (75°F)
- Maximum altitude: 3,050 m (10,000 ft) & 5°C to 28°C (41°F
to 82°F)
- Maximum rate of temperature change: 20°C/hr (68°F/hr) for hard
disk drives
Water requirement:
- Minimum water flow rate: 6.0 liters per minute per chassis, assuming
1.0 lpm per compute tray with 6 trays per chassis (1 tray consists
of 2 compute nodes)
- Inlet Water Temperature: 18 °C to 45 °C (64°F to 113°F) for all
processors up to and including 145 W TDP
- Inlet Water Temperature: 18 °C to 35 °C (64°F to 95°F) for processors
at 165 W TDP (E5-2698A v3)
- Maximum pressure: 4.4 bars
Note: The water required to initially fill the system side cooling
loop must be reasonably clean, bacteria-free water (<100 CFU/ml)
such as de-mineralized water, reverse osmosis water, de-ionized water,
or distilled water. The water must be filtered with an in-line 50
micron filter (approximately 288 mesh). The water must be treated
with anti-biological and anti-corrosion measures. Refer to Water Treatment
Specification (part number 00J0351).
Particulate contaminationAttention:
- Design to ASHRAE Class A3, temperature: 36°C to 40°C (96.8°F to
104°F), with relaxed support:
- Support cloud such as workload with no performance degradation
acceptable (turbo-off)
- Under no circumstance, can any combination of the worst case workload
and configuration result in system shutdown or design exposure at
40°C
- The worst case workload (such as linpack and turbo-on) may have
performance degradation
- Airborne particulates and reactive gases acting alone or in combination
with other environmental factors such as humidity or temperature might
pose a risk to the water-cooled technology tray. For information about the limits for particulates
and gases, see Particulate contamination.
Heat output:
Approximate heat output:
- Minimum configuration: 143 BTU per hour (42 watts)
- Maximum configuration: 1733 BTU per hour (508 watts)
Electrical input:
- Sine-wave input (50-60 Hz) required
- Input voltage low range:
- Minimum: 100 V AC
- Maximum: 127 V AC
- Input voltage high range:
- Minimum: 200 V AC
- Maximum: 240 V AC
- Input kilovolt-amperes (kVA), approximately:
- Minimum: 0.042 kVA
- Maximum: 0.508 kVA